CFPS practice question 2 of 25
Fire alarm systems audible appliances ratings are usually stated as a sound pressure level (SPL) at what distance?
Full set: 189 questionsThe sound pressure level (SPL) rating for fire alarm audible appliances is standardized to ensure consistent and reliable system design. According to NFPA 72, Annex A, the sound output for these devices is measured in an anechoic chamber at a distance of 10 ft (3.05 m). This standardized rating provides a baseline for designers to calculate the effective sound level at various locations within a protected space, accounting for sound attenuation over distance and ambient noise levels. This allows for proper verification that the required sound levels, such as 15 dBA above average ambient sound level, are met throughout the occupiable area.
A. 1 ft (0.31 m): This distance is too close for a practical, standardized rating and would not be representative of performance in a typical room.
C. 15 ft (4.57 m): This is not the standard measurement distance. The requirement is often to achieve a certain sound level above ambient, not to rate the device at this distance.
D. 20 ft (6.10 m): This is not the industry standard distance for rating the sound output of the notification appliance itself.
1. NFPA 72®, National Fire Alarm and Signaling Code, 2022 Edition.
Section A.18.4.1.1: "The sound level of an installed audible notification appliance is the sound pressure level (SPL) produced by that appliance measured at a specific location. The sound output of an audible notification appliance is the SPL measured in an anechoic chamber at a distance of 10 ft (3 m)..."
2. SFPE Handbook of Fire Protection Engineering, 5th Edition.
Chapter 59, "Occupant Evacuation and Notification," Section 59.5.1, Audible Notification: This section discusses the design of audible notification systems and implicitly relies on the standard manufacturer ratings, which are based on measurements at 10 ft (3 m) to perform sound level calculations.
3. Oklahoma State University, School of Fire Protection and Safety Engineering Technology.
Courseware for FST 3433, Fire Alarm Systems Design: Course materials on notification appliance design consistently specify that device dBA ratings are provided by manufacturers based on measurements taken at 10 feet. This is a fundamental parameter for all subsequent SPL calculations.
Keep practicing
Take the free CFPS practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CFPS practice questions
- Question 1What is the minimum pipe diameter size for direct discharge of steam inside a water tank?
- Question 3What temperature measurement device consists of a pair of wires of different metals or al…
- Question 4Large quantities of flammable or combustible liquids (all classes) are best transferred
- Question 5The coefficient of discharge of a fire hydrant when the outlet is smooth and well-rounded…
- Question 6What is the occupancy factor used by the Insurance Services Office (ISO) for computing re…
- Question 7The minimum carbon dioxide design concentration for extinguishment of an ethylene fire is