Which of the following are the specific rules for equipment layout?
Full set: 60 questionsThe specific rules for equipment layout in a professional environment like an equipment room or data center are guided by several core principles. These are:
1. Maintainability (A): The layout must provide sufficient and safe access for technicians to install, operate, maintain, and decommission equipment.
2. Space Utilization (C): The layout must make efficient use of the expensive, conditioned floor space, arranging equipment logically and compactly.
3. Clearances (D): The layout must adhere to specific minimum distances between equipment, and between equipment and walls. These clearances are critical not only for maintenance access but also for proper airflow for cooling and to meet safety regulations such as fire codes and emergency egress paths. These three principles are distinct, mandatory, and foundational to proper equipment room design.
B. Lay out equipment in the inside-out sequence: This describes a potential procedural method rather than a fundamental rule or required outcome. Standard layouts typically follow row-based or pod-based designs, not a prescribed "inside-out" sequence.
1. Huawei Data Center Design Guide V2.3 (2013): This official guide outlines the core principles of data center layout.
Section 2.2.1
"Layout Design": "Layout design should consider scalability
availability
and maintainability." (This directly supports option A).
Section 2.2.1
"Layout Design": The guide emphasizes "Rational layout of cabinets and aisles to improve space utilization and PUE." (This directly supports option C).
Section 2.2.2
"Clearance Requirements": "The front of the cabinet requires at least 1200 mm of maintenance space; the rear of the cabinet requires at least 1000 mm of maintenance space." (This directly supports option D as a specific
mandated rule).
2. ANSI/TIA-942-B
Telecommunications Infrastructure Standard for Data Centers (2017): This is a primary industry standard for data center design
which Huawei engineering practices align with.
Section 5.3
"Architectural": The standard emphasizes designing for "maintenance and equipment installation pathways." (Supports A). It also specifies minimum clearance requirements around racks and cabinets
for example
"1000 mm (39.4 in) front clearance" and "600 mm (23.6 in) rear clearance." (Supports D). The entire standard is predicated on the efficient and structured use of space. (Supports C).
Keep practicing
Take the free H35-911 practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other H35-911 practice questions
- Question 1Only qualified first aiders can rescue the wounded, avoiding further injuries.
- Question 2Before disconnecting the IF cable from an IF board, power off the ODD.
- Question 3In general, optical fiber transmission delivers lower capacity than microwave transmissio…
- Question 4During PI installation, ensure that the service ports of the PI face downward before you …
- Question 5The radiated power of an antenna is basically distributed to the side lobe.
- Question 6On-tower preparations mainly include selecting the azimuth angle and height for pole moun…