API-SIEE practice question 1 of 10
According to IEEE 841, terminal boxes for voltages above 1000 V or for frame sizes exceeding 449T at 1000 V shall be provided with:
Full set: 110 questionsThe IEEE 841 standard is focused on safety, reliability, and ruggedness for motors in severe-duty applications. For higher voltages (>1000 V) or large frame sizes (>449T), the potential fault energy is significantly greater. The standard mandates a separate, grounded terminal box for the neutral leads to physically isolate them from the high-voltage phase connections. This design feature enhances safety by containing potential faults, prevents phase-to-neutral faults within the main conduit box, and simplifies the process of making secure connections during installation and maintenance.
(Note: As the specific incorrect options were not provided, this section addresses other plausible but incorrect motor features based on the context.) A pressure relief device: This is a specific requirement for explosion-proof (XP) enclosures used in hazardous locations, not a general requirement for all IEEE 841 motors meeting the specified voltage/frame size criteria. Phase-separating barriers: While often used in high-voltage terminal boxes as a good design practice to prevent phase-to-phase faults, the explicit and mandatory requirement cited in the standard for this specific condition is the separate neutral box. A desiccant breather: This is an accessory used to prevent moisture ingress into bearing housings or enclosures in high-humidity environments and is not related to the electrical termination requirements based on voltage or frame size.
1. IEEE Std 841™-2021, IEEE Standard for Petroleum and Chemical Industry—Premium-Efficiency, Severe-Duty, Totally Enclosed Fan-Cooled (TEFC) Squirrel Cage Induction Motors—Up to and Including 370 kW (500 hp).
Section 6.3.1.3 Terminal boxes, states: "For voltages above 1000 V, or for frame sizes exceeding 449T at 1000 V, a separate grounded terminal box shall be provided for the neutral leads."
2. GE Industrial Motors, IEEE 841 X$D Ultra® Motors Technical Catalog, GET-8115, 2015.
Page 4, "Construction Features" table, under "Conduit Box": The document specifies that for "MV (Medium Voltage) and 449 frame and above," the design includes a "Separate neutral box," confirming adherence to the standard's requirement.
3. Penrose, H., "Motor Standards: A Practical Summary of Their Key Elements," Proceedings of the 35th Annual Conference of the Electrical Generating Systems Association (EGSA), March 2000.
This paper discusses various motor standards, including IEEE 841. In its review of severe-duty motor construction, it highlights specific safety and reliability features, such as the isolation of neutral connections in high-power applications as a key differentiator for ensuring operational integrity in demanding industrial environments.
Keep practicing
Take the free API-SIEE practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other API-SIEE practice questions
- Question 2Machine vibration measurement using non contacting probes are taken:
- Question 3According to API 541, subsequent to completion of manufacture and testing, the vendor sha…
- Question 4Positive-pressurization and purging are based on the principle that an enclosure or room …
- Question 5According to NFPA 70, an insulated conductor used within a switchboard or switchgear shal…
- Question 6According to IEEE C57.12.00, a durable, metal, name plate shall be affixed to each transf…
- Question 7Which referenced standard in the guide applies to metal-enclosed low-voltage power circui…