CDCS practice question 2 of 25

What is a potential disadvantage of using a hypoxic-based fire suppression system as a fire extinguishing system?

Full set: 120 questions
Answer options
A: It can only be used in computer rooms which have sufficient air changes per hour.
B: The gas containers need to be close to the hazard area.
C: It can only be used in non-continuous occupied areas. Correct answer
D: It can only be used in computer rooms where you have sufficient positive pressure.
Correct Answer:
C. It can only be used in non-continuous occupied areas.
Explanation

Hypoxic-based (or oxygen reduction) fire suppression systems work by continuously maintaining a low oxygen concentration (typically 15-17%) in a protected space. While this atmosphere is breathable and considered safe for short-term human exposure for healthy individuals, it is not suitable for continuous or long-term occupancy. Health and safety regulations, such as those from OSHA (Occupational Safety and Health Administration) and equivalent European bodies, impose strict limits on exposure duration to such environments. This fundamental operational characteristic restricts their use to areas with intermittent human presence, like data centers, archives, and museums, making this a significant disadvantage for continuously occupied spaces.

Why Incorrect

A. High air changes per hour would be a detriment, as the system would need to constantly inject more inert gas to compensate for the oxygen-rich air entering the room, making it inefficient.
B. The gas containers for hypoxic systems can be located in a central storage area and the gas can be piped over considerable distances to the protected space, so proximity is not a requirement.
D. The primary requirement for a hypoxic system is a well-sealed room with a low air leakage rate to maintain the gas concentration, not necessarily positive pressure.

References

1. EN 50600-2-5:2016, Information technology — Data centre facilities and infrastructures — Part 2-5: Security systems. Section 6.3.3.3, "Oxygen reduction systems," states: "A risk assessment shall be carried out for each installation... The system creates an environment which is not suitable for a permanent working area." This directly confirms that the system is intended for non-continuously occupied areas.

2. TIA-942-B, Telecommunications Infrastructure Standard for Data Centers. Annex G, Section G.3.2.2, "Gaseous Suppression," discusses the safety of various agents. For inert gas systems that reduce oxygen, it emphasizes that design concentrations must be safe for human exposure based on the time required for egress, implicitly acknowledging that prolonged occupation is not the intended use case.

3. Uptime Institute, (2018). Tier Standard: Topology. While not a design guide, the standard's principles for concurrent maintainability and fault tolerance require consideration of life safety systems. The operational constraints of hypoxic systems, including limitations on personnel access and exposure time, are critical factors in the operational sustainability and risk profile of a facility, reinforcing their suitability only for areas not permanently staffed.