CWBSP practice question 27 of 35
A sprinkler system has been installed with 100 sprinklers. What is the minimum number of spare sprinklers to be provided?
Full set: 100 questionsAccording to NFPA 13, Standard for the Installation of Sprinkler Systems, a stock of spare sprinklers must be maintained on the premises. The required quantity is based on the total number of sprinklers installed in the system. For a facility with fewer than 300 sprinklers, the standard mandates that a minimum of six spare sprinklers be provided. Since the system in question has 100 sprinklers, it falls into this category, making six the correct minimum number of spares required.
A. 3: This is incorrect because NFPA 13 establishes an absolute minimum of six spare sprinklers, regardless of how small the system is.
C. 9: This is an arbitrary number not specified in the NFPA 13 spare sprinkler requirement table for any system size.
D. 12: This is the minimum number of spare sprinklers required for systems with 300 to 1000 sprinklers, which is a larger system than described.
1. National Fire Protection Association (NFPA). (2022). NFPA 13: Standard for the Installation of Sprinkler Systems. Section 16.2.7.3 and Table 16.2.7.3, "Number of Spare Sprinklers."
2. SFPE. (2016). SFPE Handbook of Fire Protection Engineering (5th ed.). Springer. Chapter 21, "Automatic Sprinkler Systems," Section 21.5.1.2, "Spare Sprinklers." (This section discusses and confirms the requirements outlined in NFPA 13). DOI: https://doi.org/10.1007/978-1-4939-2562-421
Keep practicing
Take the free CWBSP practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CWBSP practice questions
- Question 1An 8 in. (200 mm) Schedule 40 steel main is to be supported from a trapeze hanger. The tr…
- Question 2What is the minimum calculated design area for a dry system protecting a light hazard att…
- Question 3A paddle-type water flow alarm indicator shall be installed only in
- Question 4What standard applies for underground malleable iron threaded fittings of Class 150?
- Question 5In areas using HVLS fans, where must the fans be located in regards to sprinkler placemen…
- Question 6What piping material is acceptable for the suction and discharge piping pressure maintena…