An 8 in. (200 mm) Schedule 40 steel main is to be supported from a trapeze hanger. The trapeze hanger is to span between two joists which are 7.5 ft (2.3 m) apart. What is the minimum size of steel pipe the trapeze member is to be made of?
Full set: 100 questionsThe minimum size for a trapeze hanger member is determined by the size of the pipe it supports and the span of the trapeze. According to NFPA 13, Table 17.4.4.1.3, for an 8 in. (200 mm) pipe being supported, and a trapeze span of 7.5 ft (2.3 m), the next largest span in the table, 8 ft (2.4 m), must be used. The intersection of the row for an 8 in. supported pipe and the column for an 8 ft span specifies a minimum trapeze member size of 3 in. (80 mm) Schedule 40 steel pipe.
A. 2.5 in. (65 mm) Schedule 40 steel pipe: This size is insufficient. Per the NFPA 13 table, a 2.5 in. trapeze pipe is only adequate for a maximum span of 6 ft (1.8 m) when supporting an 8 in. main.
C. 2.5 in. (65 mm) Schedule 10 steel pipe: This option is incorrect due to both insufficient diameter for the span and the incorrect pipe schedule, which is less robust than the required Schedule 40.
D. 3 in. (80 mm) Schedule 10 steel pipe: While the diameter is correct, the pipe schedule is not. The prescriptive requirements in the NFPA 13 table are based on Schedule 40 pipe, which has a thicker wall than Schedule 10.
1. NFPA 13, Standard for the Installation of Sprinkler Systems, 2022 Edition, Table 17.4.4.1.3, "Trapeze Hanger Sizing for Steel Pipe."
2. NFPA 13, Standard for the Installation of Sprinkler Systems, 2019 Edition, Table 17.4.4.1.3, "Trapeze Hanger Sizing for Steel Pipe."
3. NFPA 13, Handbook for the Standard for the Installation of Sprinkler Systems, 2019 Edition, Chapter 17, Section 17.4.4.1, "The size of the trapeze member is determined from Table 17.4.4.1.3 based on the size of the pipe being supported and the span of the trapeze."
Keep practicing
Take the free CWBSP practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CWBSP practice questions
- Question 2What is the minimum calculated design area for a dry system protecting a light hazard att…
- Question 3A paddle-type water flow alarm indicator shall be installed only in
- Question 4What standard applies for underground malleable iron threaded fittings of Class 150?
- Question 5In areas using HVLS fans, where must the fans be located in regards to sprinkler placemen…
- Question 6What piping material is acceptable for the suction and discharge piping pressure maintena…
- Question 7A 4.2 K-factor sprinkler must deliver 17 gpm (692 mm/min). What pressure is required?