CWBSP practice question 7 of 35
A 4.2 K-factor sprinkler must deliver 17 gpm (692 mm/min). What pressure is required?
Full set: 100 questionsThe relationship between flow rate (Q), pressure (P), and a sprinkler's orifice constant (K-factor) is defined by the hydraulic formula Q = K√P. To find the required pressure, this formula must be rearranged to solve for P, resulting in P = (Q/K)². Given: Flow (Q) = 17 gpm K-factor (K) = 4.2 Calculation: P = (17 gpm / 4.2)² P = (4.0476)² P ≈ 16.38 psi Therefore, a pressure of 16.38 psi is required to deliver 17 gpm from a 4.2 K-factor sprinkler.
A. 4.52 psi (0.31 bar): This value is the result of an incorrect mathematical calculation and does not follow the standard hydraulic formula P = (Q/K)².
B. 9.22 psi (0.63 bar): This result is mathematically incorrect. It may stem from a misapplication of the formula, such as incorrectly manipulating the square root or the variables.
D. 36.86 psi (2.54 bar): This value is significantly higher than the correct pressure and represents a substantial error in applying the hydraulic calculation formula.
1. NFPA 13, Standard for the Installation of Sprinkler Systems (2022 ed.). Section 28.2.2.1, "Sprinkler Discharge," explicitly provides the formula for determining the pressure (p) required for a specific flow (q) from a sprinkler with a known K-factor (k): p = (q/k)².
2. SFPE, Handbook of Fire Protection Engineering (5th ed.). Chapter 21, "Automatic Sprinkler System Calculations," Section 21.3.1, "Hydraulic Calculation Principles." This section details the fundamental orifice flow equation used for sprinkler calculations as Q = K√P, which is the basis for the calculation performed. (DOI: 10.1007/978-1-4939-2562-421).
Keep practicing
Take the free CWBSP practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CWBSP practice questions
- Question 1An 8 in. (200 mm) Schedule 40 steel main is to be supported from a trapeze hanger. The tr…
- Question 2What is the minimum calculated design area for a dry system protecting a light hazard att…
- Question 3A paddle-type water flow alarm indicator shall be installed only in
- Question 4What standard applies for underground malleable iron threaded fittings of Class 150?
- Question 5In areas using HVLS fans, where must the fans be located in regards to sprinkler placemen…
- Question 6What piping material is acceptable for the suction and discharge piping pressure maintena…