CWBSP practice question 8 of 35
If a 2,000 ft2 (186 m2) design area is selected, what design density is required for standard spray, high temperature sprinklers protecting Class IV commodities on a back-to-back shelf storage configuration to 14 ft (4.26 m)?
Full set: 100 questionsThe key to this question is the term "back-to-back shelf storage." When shelves are placed back-to-back without a solid, continuous vertical barrier, a longitudinal flue space is created. This configuration behaves like double-row rack storage in a fire scenario. Therefore, the more stringent design criteria for rack storage from NFPA 13 must be applied, not the criteria for general shelf storage. Per NFPA 13, Table 16.2.1.3.1 (2019 Edition), for Class IV commodities in double-row racks stored up to 20 ft (6.1 m), the required design density is 0.30 gpm/ft² over a 2,000 ft² design area. The option 0.295 gpm/ft² (12.0 mm/min) is the closest value to this requirement. The use of high-temperature sprinklers allows for a reduction in the design area, but it does not change the design density itself.
A. 0.19 gpm/ft2 (7.8 mm/min) This density is too low. It corresponds to Class II commodities under the shelf storage criteria (Curve C), which is incorrect for the specified Class IV commodity.
B. 0.25 gpm/ft2 (10.2 mm/min) This density would be correct for standard shelf storage (Curve E). However, it fails to account for the increased fire hazard of the back-to-back configuration, which must be treated as rack storage.
D. 0.385 gpm/ft2 (15.6 mm/min) This density is excessively high for Class IV commodities. It is more aligned with the protection requirements for certain configurations of Group A plastics, not Class IV materials.
1. NFPA 13, Standard for the Installation of Sprinkler Systems, 2019 Edition.
Table 16.2.1.3.1, "CMDA Sprinkler Protection Criteria for Single-, Double-, and Multiple-Row Racks for Class I Through Class IV Commodities Stored up to 20 ft (6.1 m) in Height." This table explicitly lists a required density of 0.30 gpm/ft² over a 2000 ft² area for Class IV commodities.
Section A.3.9.2.8, Rack. The annex commentary clarifies the distinction between shelf and rack storage, noting that shelving arrangements that create flue spaces, such as back-to-back shelves without solid backing, should be protected as racks.
2. SFPE, The SFPE Handbook of Fire Protection Engineering, 5th Edition.
Chapter 41, "Automatic Sprinkler System Design," Section 41.6.3.2, "Control Mode Density Area (CMDA) Design for Storage." This section discusses how storage configuration, including the presence of flue spaces in rack-like arrangements, dictates the selection of the appropriate design density from NFPA 13 tables. It reinforces that configurations mimicking racks require rack storage protection criteria. (DOI: https://doi.org/10.1007/978-1-4939-2565-041)
3. Worcester Polytechnic Institute (WPI),
Keep practicing
Take the free CWBSP practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CWBSP practice questions
- Question 1An 8 in. (200 mm) Schedule 40 steel main is to be supported from a trapeze hanger. The tr…
- Question 2What is the minimum calculated design area for a dry system protecting a light hazard att…
- Question 3A paddle-type water flow alarm indicator shall be installed only in
- Question 4What standard applies for underground malleable iron threaded fittings of Class 150?
- Question 5In areas using HVLS fans, where must the fans be located in regards to sprinkler placemen…
- Question 6What piping material is acceptable for the suction and discharge piping pressure maintena…