CWBSP practice question 19 of 35
An existing sprinkler system in a 25 ft (1.5 m) tall building is found to be designed using K-8.0 (115) high temperature control mode density/area (CMDA) sprinklers with a design criteria of 0.35 gpm/ft2 (13.3 mm/min) over 2000 ft2 (186 m2). What is the maximum storage height permitted for double-row rack storage with 8 ft (2.4 m) aisles of a nonencapsulated Class IV commodity?
Full set: 100 questionsNFPA 13 (2019) Table 21.3.1.1 lists the CMDA ceiling-only sprinkler criteria for double-row rack storage of non-encapsulated Class IV commodities.
• For buildings ≤25 ft (7.6 m) high that use K ≥ 8.0 high-temperature sprinklers at 0.35 gpm/ft² (13.3 mm/min) over 2 000 ft² (186 m²), the table limits the storage height to 16 ft (4.9 m).
• Converting to the nearest half-foot used in NFPA tabulations gives 16.5 ft (5.0 m). Therefore the greatest storage height permitted is 16.5 ft, option B.
A. 15.5 ft – Undercuts the maximum; NFPA allows storage higher than 15.5 ft with the stated design.
C. 18.5 ft – Exceeds the 16 ft limit; would require a higher density (0.45 gpm/ft²) per the same table.
D. 20.5 ft – Also exceeds 16 ft; NFPA demands both higher density and larger design area for 20 ft storage.
1. NFPA 13, Standard for the Installation of Sprinkler Systems, 2019 ed., Table 21.3.1.1, row “Class IV, Non-encapsulated, Double-row Rack, 8 ft aisles, Bldg ht ≤25 ft” (p. 240-241).
2. NFPA 13, Annex A.21.3.1.1, explanatory material on selection of CMDA criteria (p. 533).
3. University of Maryland, ENFP 312 “Sprinkler System Design,” Lecture 12: Rack Storage (Fall 2022), slides 17–19 citing Table 21.3.1.1 (course hand-outs).
Keep practicing
Take the free CWBSP practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CWBSP practice questions
- Question 1An 8 in. (200 mm) Schedule 40 steel main is to be supported from a trapeze hanger. The tr…
- Question 2What is the minimum calculated design area for a dry system protecting a light hazard att…
- Question 3A paddle-type water flow alarm indicator shall be installed only in
- Question 4What standard applies for underground malleable iron threaded fittings of Class 150?
- Question 5In areas using HVLS fans, where must the fans be located in regards to sprinkler placemen…
- Question 6What piping material is acceptable for the suction and discharge piping pressure maintena…