CWBSP practice question 11 of 35
Assuming that the sprinkler is listed for such use, what is the maximum deflector distance for standard spray horizontal sidewall sprinklers from the ceiling under non- and limited-combustible ceilings?
Full set: 100 questionsAccording to NFPA 13, Standard for the Installation of Sprinkler Systems, the standard placement for sidewall sprinkler deflectors is between 4 in. (100 mm) and 6 in. (150 mm) below the ceiling. However, an exception is made for horizontal sidewall sprinklers installed under non-combustible or limited-combustible ceilings. If the sprinklers are specifically listed for this application, they are permitted to be located 6 in. to 12 in. (150 mm to 300 mm) below the ceiling. The question asks for the maximum distance under these specific conditions, which is 12 in. (300 mm).
A. 4 in. (100 mm) is the minimum distance for standard sidewall sprinkler placement, not the maximum for this specific scenario.
B. 6 in. (150 mm) is the maximum distance for standard placement but the minimum distance allowed under this specific exception.
D. 18 in. (450 mm) exceeds the maximum permitted distance specified in the standard for this application.
1. NFPA 13, Standard for the Installation of Sprinkler Systems (2022 Edition).
Section 9.3.4.1.2: "Horizontal sidewall sprinklers shall be permitted to be located 6 in. to 12 in. (150 mm to 300 mm) below noncombustible or limited-combustible ceilings where listed for such use." This section directly states the allowable range, with 12 in. being the maximum.
2. NFPA 13, Handbook for the Standard for the Installation of Sprinkler Systems (2019 Edition).
Exhibit 9.15: This exhibit and the accompanying text for Section 9.3.5.1.2 explain that certain listed horizontal sidewall sprinklers have been tested and proven effective at greater distances (up to 12 in.) from noncombustible ceilings, allowing for this specific installation parameter.
3. Oklahoma State University, College of Engineering, Architecture and Technology. Fire Protection & Safety Engineering Technology Course FST 3333 - Fire Sprinkler Systems.
Module on Sprinkler Installation Requirements: Course materials covering NFPA 13 sprinkler positioning rules detail the specific exceptions for sidewall sprinklers, including the 6 in. to 12 in. placement rule below non-combustible ceilings when using sprinklers listed for that purpose.
Keep practicing
Take the free CWBSP practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CWBSP practice questions
- Question 1An 8 in. (200 mm) Schedule 40 steel main is to be supported from a trapeze hanger. The tr…
- Question 2What is the minimum calculated design area for a dry system protecting a light hazard att…
- Question 3A paddle-type water flow alarm indicator shall be installed only in
- Question 4What standard applies for underground malleable iron threaded fittings of Class 150?
- Question 5In areas using HVLS fans, where must the fans be located in regards to sprinkler placemen…
- Question 6What piping material is acceptable for the suction and discharge piping pressure maintena…