For an Extra Hazard Group 1 remote area of 2,500 ft2 (232.25 m2) using fire sprinklers with a coverage area of 92 ft2 (8.547 m2), how many gallons per minute of water are required per sprinkler?
Full set: 100 questionsThe required flow per sprinkler is calculated by multiplying the design density by the sprinkler coverage area (Q = d × A). According to the NFPA 13 Density/Area curves, an Extra Hazard Group 1 occupancy with a design area of 2,500 ft² requires a minimum design density of 0.30 gpm/ft². The calculation is as follows: Flow per sprinkler = 0.30 gpm/ft² × 92 ft² = 27.6 gpm. Among the given choices, 26.8 gpm is the closest value to the correctly calculated flow rate of 27.6 gpm. The minor discrepancy is likely due to rounding or a slight inaccuracy in the question's options.
A. This flow rate is too low and results from a density significantly below the 0.30 gpm/ft² required by the standard for this hazard and design area.
C. This flow rate is significantly higher than the calculated 27.6 gpm requirement for an Extra Hazard Group 1 occupancy.
D. This flow rate (36.8 gpm) is the correct calculation for an Extra Hazard Group 2 occupancy (0.40 gpm/ft² × 92 ft²), not the specified Group 1.
1. NFPA 13, Standard for the Installation of Sprinkler Systems (2022 Edition). Figure 27.2.3.1.1, "Density/Area Curves." The curve for Extra Hazard Group 1 explicitly shows a density of 0.30 gpm/ft² for a design area of 2,500 ft².
2. NFPA 13, Standard for the Installation of Sprinkler Systems (2019 Edition). Figure 19.3.1.1, "Density/Area Curves." This figure provides the same density value of 0.30 gpm/ft² for Extra Hazard Group 1 at 2,500 ft².
3. SFPE, Handbook of Fire Protection Engineering (5th Edition). Chapter 23, "Automatic Sprinkler System Calculations," Section 23.4.2. This section details the density/area design method, confirming the calculation methodology (Q = d × Aₛ). (DOI: https://doi.org/10.1007/978-1-4939-2562-423)
Keep practicing
Take the free CWBSP practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CWBSP practice questions
- Question 1An 8 in. (200 mm) Schedule 40 steel main is to be supported from a trapeze hanger. The tr…
- Question 2What is the minimum calculated design area for a dry system protecting a light hazard att…
- Question 3A paddle-type water flow alarm indicator shall be installed only in
- Question 4What standard applies for underground malleable iron threaded fittings of Class 150?
- Question 5In areas using HVLS fans, where must the fans be located in regards to sprinkler placemen…
- Question 6What piping material is acceptable for the suction and discharge piping pressure maintena…