CWBSP practice question 21 of 35
For an Ordinary Hazard with a design area of 1,500 ft2 (140 m2), what is the minimum number of standard pendent sprinklers required?
Full set: 100 questionsThe minimum number of sprinklers required in a design area is calculated by dividing the total design area by the maximum allowable protection area per sprinkler for the specific hazard classification. According to NFPA 13, for an Ordinary Hazard occupancy using standard spray sprinklers, the maximum protection area per sprinkler is 130 ft². The calculation is as follows: Design Area / Maximum Area per Sprinkler = 1,500 ft² / 130 ft² = 11.54 sprinklers. Since a fraction of a sprinkler cannot be installed, the result must be rounded up to the next whole number. Therefore, a minimum of 12 sprinklers are required to cover the design area.
B. 14 sprinklers: This number is higher than the calculated minimum and would result from using a smaller, non-standard coverage area per sprinkler (approx. 107 ft²).
C. 18 sprinklers: This is significantly more than the minimum required and would represent an inefficient design for the specified hazard and area.
D. 20 sprinklers: This number is substantially greater than the minimum required by the standard, leading to an unnecessarily conservative and costly installation.
1. NFPA 13, Standard for the Installation of Sprinkler Systems (2022 Edition).
Table 10.2.4.2.1(a) "Protection Areas and Maximum Spacing for Standard Pendent and Upright Spray Sprinklers for System Design." This table explicitly states that for an "Ordinary Hazard" occupancy, the maximum "Protection Area of Coverage per Sprinkler" is 130 ft² (12.1 m²).
Section 27.2.2.1.3 "The number of sprinklers in the design area shall be determined by dividing the size of the design area (ft² or m²) by the area of sprinkler protection (Aₛ)." This section provides the methodology for the calculation.
Keep practicing
Take the free CWBSP practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CWBSP practice questions
- Question 1An 8 in. (200 mm) Schedule 40 steel main is to be supported from a trapeze hanger. The tr…
- Question 2What is the minimum calculated design area for a dry system protecting a light hazard att…
- Question 3A paddle-type water flow alarm indicator shall be installed only in
- Question 4What standard applies for underground malleable iron threaded fittings of Class 150?
- Question 5In areas using HVLS fans, where must the fans be located in regards to sprinkler placemen…
- Question 6What piping material is acceptable for the suction and discharge piping pressure maintena…