CWBSP practice question 30 of 35

What is the minimum calculated design area for a light hazard sprinkler system protecting an open office space with a noncombustible acoustic ceiling tile installed 6 in. (150 mm) below the bottom of solid wood joists?

Full set: 100 questions
Answer options
A: 900 ft2 (83.6 m2)
B: 1,500 ft2 (139.35 m2) Correct answer
C: 1,950 ft2 (181.1 m2)
D: 3,000 ft2 (278.7 m2)
Correct Answer:
B. 1,500 ft2 (139.35 m2)