What is the minimum temperature rating of ceiling sprinklers in roll paper stored at 15 ft. (4.6 m) or less?
Full set: 100 questionsNFPA 13 treats roll-paper piles as a special-storage arrangement. Where the storage height does not exceed 15 ft (4.6 m), §24.13.4.1 (2022 ed.)/§20.4.4.1 (2019 ed.) states that ceiling sprinklers “shall be ordinary-temperature sprinklers.” Ordinary-temperature classification is defined in Table 7.2.4.1 as nominal 155 °F (68 °C). Option C (150 °F / 66 °C) is the only choice that represents this ordinary-temperature requirement and therefore is the minimum rating permitted for the described storage arrangement.
A. 100 °F (38 °C) – Low-temperature classification; NFPA 13 does not allow low-temperature sprinklers in roll-paper storage because they can open prematurely from routine heat.
B. 135 °F (57 °C) – Lower end of ordinary class, but NFPA 13 specifies the 155 °F nominal sprinkler for this hazard; 135 °F is not listed as the acceptable minimum.
D. 175 °F (79 °C) – Intermediate-temperature sprinklers are required only when roll-paper storage exceeds 15 ft or for in-rack locations, not for ≤15 ft ceiling protection.
1. NFPA 13, Standard for the Installation of Sprinkler Systems, 2022 ed., Sec. 24.13.4.1, p. 347 – “Sprinklers shall be ordinary-temperature for storage ≤4.6 m.”
2. NFPA 13, Standard for the Installation of Sprinkler Systems, 2022 ed., Table 7.2.4.1, p. 66 – Ordinary-temperature nominal rating 155 °F (68 °C).
3. NFPA 13, Standard for the Installation of Sprinkler Systems, 2019 ed., Sec. 20.4.4.1 & Table 20.4.4(a), p. 283 – Identical ordinary-temperature requirement for roll-paper ≤15 ft.
4. J. Crawford, “Storage Occupancies—Special Commodities,” Kansas State Univ. FPP 221 Course Notes, 2021, slide 34 – Summarizes NFPA 13 roll-paper sprinkler temperature criteria (ordinary ≤15 ft, intermediate >15 ft).
Keep practicing
Take the free CWBSP practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CWBSP practice questions
- Question 1An 8 in. (200 mm) Schedule 40 steel main is to be supported from a trapeze hanger. The tr…
- Question 2What is the minimum calculated design area for a dry system protecting a light hazard att…
- Question 3A paddle-type water flow alarm indicator shall be installed only in
- Question 4What standard applies for underground malleable iron threaded fittings of Class 150?
- Question 5In areas using HVLS fans, where must the fans be located in regards to sprinkler placemen…
- Question 6What piping material is acceptable for the suction and discharge piping pressure maintena…