API-SIEE practice question 9 of 10
Circuit breakers over 1000 V equipped with stored energy mechanisms shall perform which of the following functions?
Full set: 110 questionsNEC 2023 Article 240.92(C) stipulates that any circuit breaker rated over 1000 V that is equipped with a stored-energy operating mechanism “shall automatically recharge the mechanism after each operation so that the breaker is immediately ready for the next duty cycle.” The purpose is to ensure the breaker can perform the standard O-CO (open-close-open) duty without operator intervention, maintaining reliability for high-energy fault interruption and reclosing sequences. Therefore, the mandatory function is automatic re-charging of the stored-energy mechanism after every opening or closing operation.
A. Manual-only charging violates NEC 240.92(C) automatic-recharge requirement.
B. Trip-free action is desirable but not mandated by the stored-energy clause.
C. Having charge only while control power is present defeats the automatic feature and fails NEC mandate.
1. NFPA 70 (NEC) 2023, Art. 240.92(C) “Stored-Energy Mechanisms,” p. 141 (soft-copy pagination).
2. IEEE Std C37.100.1-2017, §6.2.2 “Stored-Energy Closing Duty Cycle (O-CO),” pp. 32-33.
3. IEEE Std C37.04-2018, Table 2 & §5.3, requirement for automatic re-charge capability in high-voltage breakers.
4. MIT OpenCourseWare, “High-Voltage Circuit Breakers,” Lecture 12 notes, slide 17 (discusses automatic re-charging of stored-energy mechanisms).
Keep practicing
Take the free API-SIEE practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other API-SIEE practice questions
- Question 1According to IEEE 841, terminal boxes for voltages above 1000 V or for frame sizes exceed…
- Question 2Machine vibration measurement using non contacting probes are taken:
- Question 3According to API 541, subsequent to completion of manufacture and testing, the vendor sha…
- Question 4Positive-pressurization and purging are based on the principle that an enclosure or room …
- Question 5According to NFPA 70, an insulated conductor used within a switchboard or switchgear shal…
- Question 6According to IEEE C57.12.00, a durable, metal, name plate shall be affixed to each transf…