CDCS practice question 20 of 25

What indicates the breaking capacity of a fuse or breaker?

Full set: 120 questions
Answer options
A: Mechanical strength of the casing of a fuse or breaker.
B: The maximum voltage, in case of an electrical surge, that the fuse or breaker can handle without being destroyed or causing an electric damaging arc.
C: The current at which the device will trip.
D: The current that a fuse or breaker is able to interrupt without being destroyed or causing an electric damaging arc. Correct answer
Correct Answer:
D. The current that a fuse or breaker is able to interrupt without being destroyed or causing an electric damaging arc.
Explanation

Breaking capacity, also known as the interrupting rating or fault rating, is a critical safety parameter for a protective device like a fuse or circuit breaker. It defines the maximum prospective short-circuit current that the device can safely interrupt at a rated voltage without failing catastrophically (e.g., exploding or creating a sustained, dangerous electric arc). This rating must be equal to or greater than the maximum potential fault current at the point of installation in the electrical system to ensure safety and prevent equipment damage or fire.

Why Incorrect

A. Mechanical strength of the casing relates to the physical durability of the device, not its specific electrical function of interrupting fault currents.
B. This describes the voltage rating of the device, which is the maximum voltage it can withstand, a separate parameter from its current-interrupting capability.
C. This describes the nominal or trip current rating, which is the continuous current the device can carry or the overload level at which it is designed to open the circuit.

References

1. Schneider Electric. (2005). Calculation of short-circuit currents (Cahier Technique no. 158). Section 5.2, "Breaking and making capacity," p. 26. This document states, "The breaking capacity is the highest value of current that the circuit-breaker is capable of breaking... This is a prospective short-circuit current." This directly supports the definition in option D.

2. Eaton Corporation. (2020). Interrupting Rating, Series Ratings, and Selective Coordination (Technical Data TD01200001E). Section "Interrupting Rating," p. 2. The document defines interrupting rating as: "The highest current at rated voltage that a device is intended to interrupt under standard test conditions." This confirms that the rating is about the current a device can interrupt.

3. Grainger, J. J., & Stevenson, W. D. (1994). Power System Analysis. McGraw-Hill. Chapter 10, "Symmetrical Faults," Section 10.5, "Circuit Breakers and Fuses." This university-level textbook explains that a circuit breaker's interrupting rating must exceed the maximum fault current it is expected to interrupt, aligning with the concept of safely handling a specific current level.