CFI-I practice question 9 of 35

A fully sprinklered structure containing 1,500 sprinklers requires a minimum supply of how many spare sprinklers?

Full set: 100 questions
Answer options
A: 6
B: 12
C: 18
D: 24 Correct answer
Correct Answer:
D. 24
Explanation

According to NFPA 13, Standard for the Installation of Sprinkler Systems, a specific quantity of spare sprinklers must be maintained on the premises. The required number is based on the total quantity of sprinklers installed. For a system with over 1,000 sprinklers, the standard mandates a minimum of 24 spare sprinklers. Since the facility has 1,500 installed sprinklers, it falls into this category. The stock of spare sprinklers must include all types and temperature ratings installed in the property to ensure any damaged or operated sprinkler can be promptly replaced, maintaining the system's operational readiness.

Why Incorrect

A. 6: This is the minimum number of spare sprinklers required for a system with fewer than 300 sprinklers.
B. 12: This is the minimum number of spare sprinklers required for a system with 300 to 1,000 sprinklers.
C. 18: This quantity is not a specified minimum threshold for spare sprinklers according to the NFPA 13 standard.

References

1. NFPA 13, Standard for the Installation of Sprinkler Systems, 2022 Edition. Section 19.2.8.2, "Spare Sprinklers." Table 19.2.8.2 specifies:

Fewer than 300 sprinklers: 6 spares

300 to 1000 sprinklers: 12 spares

Over 1000 sprinklers: 24 spares