CFI-I practice question 16 of 35

Prior to seeking system acceptance for a sprinkler installation, an installer shall do which of the following? I . Perform all required acceptance tests II . Complete all contractors’ material and test certificates III . Notify the AHJ of the time and date of the test IV . Complete owners' approval form and forward it to the AHJ

Full set: 100 questions
Answer options
A: I and IV
B: III and IV
C: I, II, and III Correct answer
D: II, III, and IV
Correct Answer:
C. I, II, and III
Explanation

According to NFPA 13, Standard for the Installation of Sprinkler Systems, before seeking final approval from the Authority Having Jurisdiction (AHJ), the installing contractor has several responsibilities. The contractor must conduct all required acceptance tests, such as hydrostatic and air tests, to ensure system integrity and functionality. Concurrently, the contractor must accurately complete the "Contractor’s Material and Test Certificate(s)," which documents the system components and test results. A critical procedural step is to notify the AHJ in advance of the time and date for the tests, as the AHJ often must witness them. These three actions are mandatory prerequisites for system acceptance.

Why Incorrect

A. I and IV: This option is incorrect because it omits the mandatory completion of the contractor's certificates (II) and notification of the AHJ (III), while including the non-required owner's approval form (IV).
B. III and IV: This option is incorrect as it omits the fundamental requirements to perform tests (I) and complete the contractor's certificates (II), and includes the incorrect statement about an owner's approval form (IV).
D. II, III, and IV: This option is incorrect because it includes statement IV. The installer provides documentation to the owner but is not required to complete and forward an "owner's approval form" to the AHJ.

References

1. NFPA 13, Standard for the Installation of Sprinkler Systems, 2019 Edition.

Chapter 28, Section 28.1.1: "The installing contractor shall be responsible for the following: (1) Performing all required acceptance tests... (2) Completing the contractor’s material and test certificate(s)... (3) Forwarding the certificate(s) to the authority having jurisdiction prior to asking for approval of the installation." (Supports I and II).

Chapter 28, Section 28.2.1.2: "The installing contractor shall notify the authority having jurisdiction of the time and date of the test." (Supports III).

2. Cote, A. E. (Ed.). (2021). Fire Protection Handbook (21st ed.). National Fire Protection Association.

Section 18, Chapter 2, "Installation of Sprinkler Systems," Subsection: System Acceptance: This chapter details the acceptance process, stating, "Before asking the AHJ for approval of the installation, the installing contractor is responsible for... performing all required acceptance tests... [and] completing the contractor’s material and test certificate(s)..." This text reinforces the requirements outlined in NFPA 13.

3. Oklahoma State University, Fire Protection Publications. (2015). Plans Review of Fire Protection Systems.

Chapter 4, "Acceptance Testing": This chapter discusses the procedural requirements for system acceptance, emphasizing that the contractor must complete all testing, fill out the M&T certificates, and coordinate with the AHJ for witnessing the tests before the system can be placed in service. This aligns with the requirements of NFPA 13.