CFI-I practice question 28 of 35
Which of the following systems has a quick-opening device?
Full set: 100 questionsA quick-opening device (QOD), such as an accelerator or an exhauster, is a component used almost exclusively with dry-pipe sprinkler systems. Its purpose is to reduce the time it takes for water to be delivered to an activated sprinkler head. In a dry-pipe system, the piping is filled with pressurized air or nitrogen. When a sprinkler opens, this pressure must drop sufficiently to allow the dry-pipe valve to open. A QOD senses the rapid pressure drop and sends a signal (typically pneumatic) to the dry-pipe valve, causing it to trip and release water into the piping network much faster than it would by pressure differential alone.
B. Wet-pipe system: The piping is already filled with water, so there is no inherent delivery delay that would necessitate a quick-opening device.
C. Preaction system: Activation depends on a separate detection system (e.g., smoke detectors) triggering the primary valve, not solely on air pressure loss from a sprinkler.
D. Deluge system: The deluge valve is activated by an independent detection system, and the sprinklers are already open; a QOD is not part of this design.
1. NFPA 13, Standard for the Installation of Sprinkler Systems, 2022 Edition. Section 8.2, "Dry Pipe Systems," specifically addresses the requirements for these systems. Section 8.2.4, "Quick-Opening Devices (QODs)," states in 8.2.4.1, "Where the water delivery time to the inspector's test connection exceeds the requirements of 8.2.3.1, a quick-opening device shall be provided." This section is exclusively within the chapter for dry-pipe systems.
2. SFPE Handbook of Fire Protection Engineering, 5th Edition. In Chapter 23, "Automatic Sprinkler Systems," the section on "Dry-Pipe Systems" states: "To speed the operation of the dry-pipe valve on large systems, a device called an accelerator or an exhauster is used. These devices are referred to as quick-opening devices (QODs)." (p. 779).
3. Fire Protection Handbook, 21st Edition, NFPA. Volume 2, Section 17, Chapter 2, "Types of Sprinkler Systems." The subsection on "Dry Pipe Systems" explains the operational delay and states, "To reduce the time to trip the valve, a quick-opening device (QOD) can be installed near the dry pipe valve." It further describes the function of accelerators and exhausters in this context.
Keep practicing
Take the free CFI-I practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CFI-I practice questions
- Question 1During an inspection, it is determined that the installation of a new suppression system …
- Question 2When submitting materials for plan review, the applicant has the responsibility to ensure…
- Question 3What is the maximum travel distance from point A (fire extinguisher) to point B for the o…
- Question 4All of the following information regarding a fire prevention inspection must be maintaine…
- Question 5Which of the following conditions gives an inspector the right to enter a private dwellin…
- Question 6A highly volatile liquid is best described as having a boiling point of