CFI-I practice question 28 of 35

Which of the following systems has a quick-opening device?

Full set: 100 questions
Answer options
A: Dry-pipe system Correct answer
B: Wet-pipe system
C: Preaction system
D: Deluge system
Correct Answer:
A. Dry-pipe system
Explanation

A quick-opening device (QOD), such as an accelerator or an exhauster, is a component used almost exclusively with dry-pipe sprinkler systems. Its purpose is to reduce the time it takes for water to be delivered to an activated sprinkler head. In a dry-pipe system, the piping is filled with pressurized air or nitrogen. When a sprinkler opens, this pressure must drop sufficiently to allow the dry-pipe valve to open. A QOD senses the rapid pressure drop and sends a signal (typically pneumatic) to the dry-pipe valve, causing it to trip and release water into the piping network much faster than it would by pressure differential alone.

Why Incorrect

B. Wet-pipe system: The piping is already filled with water, so there is no inherent delivery delay that would necessitate a quick-opening device.
C. Preaction system: Activation depends on a separate detection system (e.g., smoke detectors) triggering the primary valve, not solely on air pressure loss from a sprinkler.
D. Deluge system: The deluge valve is activated by an independent detection system, and the sprinklers are already open; a QOD is not part of this design.

References

1. NFPA 13, Standard for the Installation of Sprinkler Systems, 2022 Edition. Section 8.2, "Dry Pipe Systems," specifically addresses the requirements for these systems. Section 8.2.4, "Quick-Opening Devices (QODs)," states in 8.2.4.1, "Where the water delivery time to the inspector's test connection exceeds the requirements of 8.2.3.1, a quick-opening device shall be provided." This section is exclusively within the chapter for dry-pipe systems.

2. SFPE Handbook of Fire Protection Engineering, 5th Edition. In Chapter 23, "Automatic Sprinkler Systems," the section on "Dry-Pipe Systems" states: "To speed the operation of the dry-pipe valve on large systems, a device called an accelerator or an exhauster is used. These devices are referred to as quick-opening devices (QODs)." (p. 779).

3. Fire Protection Handbook, 21st Edition, NFPA. Volume 2, Section 17, Chapter 2, "Types of Sprinkler Systems." The subsection on "Dry Pipe Systems" explains the operational delay and states, "To reduce the time to trip the valve, a quick-opening device (QOD) can be installed near the dry pipe valve." It further describes the function of accelerators and exhausters in this context.