What is the pressure at a sprinkler head with a flow of 33 gpm (125 L/min) with a K-factor of 5.6 (80)?
Full set: 100 questionsThe pressure required at a sprinkler head is calculated using the formula derived from the orifice equation: P = (Q/K)², where P is the pressure in psi, Q is the flow in gallons per minute (gpm), and K is the nominal K-factor. Given the values:
- Q = 33 gpm
- K = 5.6 The calculation is as follows: P = (33 / 5.6)² P = (5.893)² P = 34.73 psi This value is rounded to 34.7 psi. The metric calculation confirms this result: P = (125 L/min / 80)² = 2.44 bar.
A. This pressure would result from a much lower flow rate (approximately 21.7 gpm) for the given K-factor, representing a significant miscalculation.
B. This pressure is an incorrect calculation and does not correspond to the relationship defined by the sprinkler discharge formula for the given parameters.
D. This pressure would require a significantly higher flow rate (approximately 41.7 gpm) through the sprinkler head with the specified K-factor.
1. NFPA 13, Standard for the Installation of Sprinkler Systems, 2022 Edition. Chapter 9, Section 9.1.2.1, "The quantity of water discharged from a sprinkler is determined by the formula q = K√p." (This formula is rearranged to P = (q/K)² to solve for pressure).
2. Society of Fire Protection Engineers (SFPE). SFPE Handbook of Fire Protection Engineering, 5th Edition. Chapter 21, "Hydraulic Calculations for Water-Based Fire Protection Systems," Section 21.3.1, "The K-Factor Formula," page 738. The text explicitly provides the formula Q = K√P.
3. Oklahoma State University, School of Fire Protection and Safety Engineering Technology. FSET 3153 - Sprinklers and Standpipes Courseware. Module on Hydraulic Calculations, which details the use of the formula P = (Q/K)² for determining required sprinkler pressure.
Keep practicing
Take the free CWBSP practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CWBSP practice questions
- Question 1An 8 in. (200 mm) Schedule 40 steel main is to be supported from a trapeze hanger. The tr…
- Question 2What is the minimum calculated design area for a dry system protecting a light hazard att…
- Question 3A paddle-type water flow alarm indicator shall be installed only in
- Question 4What standard applies for underground malleable iron threaded fittings of Class 150?
- Question 5In areas using HVLS fans, where must the fans be located in regards to sprinkler placemen…
- Question 6What piping material is acceptable for the suction and discharge piping pressure maintena…