CWBSP practice question 33 of 35
When field acceptance testing a fire pump with a variable speed pressure limiting control, the pump shall be tested in variable speed mode at
Full set: 100 questionsAccording to NFPA 20, the field acceptance test for a fire pump with a variable speed pressure limiting control must be conducted in the variable speed mode. The standard explicitly mandates that the pump's performance be verified at three critical points: no-flow (churn), 100 percent of its rated flow, and 150 percent of its rated flow. This three-point test ensures the pump and its controller can deliver the required performance across the entire operational curve while effectively limiting pressure as designed.
A. This option is incomplete as it omits the 150% rated load test, which is a mandatory point for verifying peak performance.
C. This option includes an additional test point (50%) that is not required by the standard for minimum acceptance criteria.
D. This option lists multiple test points that are not mandated by the standard for acceptance, making the procedure unnecessarily extensive.
1. NFPA 20, Standard for the Installation of Stationary Pumps for Fire Protection, 2022 Edition, Chapter 14, Section 14.2.6.2.7. This section states, "For pumps with variable speed pressure limiting control, the pump shall be tested in variable speed mode at no flow, 100 percent of rated load, and 150 percent of rated load."
Keep practicing
Take the free CWBSP practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other CWBSP practice questions
- Question 1An 8 in. (200 mm) Schedule 40 steel main is to be supported from a trapeze hanger. The tr…
- Question 2What is the minimum calculated design area for a dry system protecting a light hazard att…
- Question 3A paddle-type water flow alarm indicator shall be installed only in
- Question 4What standard applies for underground malleable iron threaded fittings of Class 150?
- Question 5In areas using HVLS fans, where must the fans be located in regards to sprinkler placemen…
- Question 6What piping material is acceptable for the suction and discharge piping pressure maintena…