LEED-AP-IDC practice question 35 of 35
A mechanical engineer needs to determine the number of carbon dioxide monitors needed for the public area of a hotel. The public area includes the…
Full set: 100 questionsLEED v4 ID+C EQ Credit “Enhanced Indoor Air Quality Strategies,” Option 2, Part C requires a carbon-dioxide sensor “in each densely occupied space (≥25 people/1 000 ft²).” ASHRAE 62.1-2010 Table 6-1 lists default occupant densities:
• Toilet/Restroom 0.50 person/m² ≈ 46 persons/1 000 ft² (densely occupied)
• Lobby 0.05 person/m² ≈ 5 persons/1 000 ft² (not dense)
• Corridor 0.05 person/m² ≈ 5 persons/1 000 ft² (not dense)
• Hotel front-desk area is typically ≤0.25 person/m² ≈ 23 persons/1 000 ft² (below threshold). Therefore, only the two public restrooms meet the LEED definition; each must have its own CO₂ monitor. Minimum monitors required = 2.
A. One – Fails to cover both densely occupied restrooms; credit cannot be earned.
C. Four – Adds monitors to lobby and corridor, which are not densely occupied; not required.
D. Five – Same over-coverage as (C) plus one extra; exceeds credit requirements without added benefit.
1. USGBC. LEED v4 for Interior Design and Construction Reference Guide, EQ Credit “Enhanced IAQ Strategies,” Option 2, Part C Carbon Dioxide Monitoring, p. 538-539.
2. ASHRAE Standard 62.1-2010, Table 6-1 “Minimum Ventilation Rates in Breathing Zone,” Occupant Density column: Toilet/Restroom 0.50 pers/m²; Lobby & Corridor 0.05 pers/m²; Front-desk/Service Counter ≤0.25 pers/m².
3. USGBC LEED v4 Definition of “Densely Occupied Space,” Glossary, p. 931.
Keep practicing
Take the free LEED-AP-IDC practice test
Ten exam-style questions with answers and explanations, plus the exam facts and study guides.
More questions
Other LEED-AP-IDC practice questions
- Question 1A mechanical engineer needs to identify spaces that are considered densely occupied accor…
- Question 2A renovation project includes both a new kitchen sink and shower and an existing lavatory…
- Question 3A project team wants to achieve Materials and Resources Credit, Building Product Disclosu…
- Question 4To satisfy the Increased Ventilation strategy in the Indoor Environmental Quality Credit,…
- Question 5A tenant implements the following strategies to reduce the amount of water used. Which st…
- Question 7What should a team focus on first to significantly improve energy performance or achieve …