LEED-AP-IDC practice question 35 of 35

A mechanical engineer needs to determine the number of carbon dioxide monitors needed for the public area of a hotel. The public area includes the…

Full set: 100 questions
A mechanical engineer needs to determine the number of carbon dioxide monitors needed for the public area of a hotel. The public area includes the hotel front desk, the hotel lobby, two public restrooms and one corridor. The aim is to achieve Indoor Environmental Quality Credit, Enhanced Indoor Air Quality Strategies, Option 2. Additional Enhanced IAQ Strategies, Part C. Carbon Dioxide Monitoring. The project's LEED AP should recommend a minimum of how many CO2 monitors?
Answer options
A: One
B: Two Correct answer
C: Four
D: Five
Correct Answer:
B. Two
Explanation

LEED v4 ID+C EQ Credit “Enhanced Indoor Air Quality Strategies,” Option 2, Part C requires a carbon-dioxide sensor “in each densely occupied space (≥25 people/1 000 ft²).” ASHRAE 62.1-2010 Table 6-1 lists default occupant densities:
• Toilet/Restroom 0.50 person/m² ≈ 46 persons/1 000 ft² (densely occupied)
• Lobby 0.05 person/m² ≈ 5 persons/1 000 ft² (not dense)
• Corridor 0.05 person/m² ≈ 5 persons/1 000 ft² (not dense)
• Hotel front-desk area is typically ≤0.25 person/m² ≈ 23 persons/1 000 ft² (below threshold). Therefore, only the two public restrooms meet the LEED definition; each must have its own CO₂ monitor. Minimum monitors required = 2.

Why Incorrect

A. One – Fails to cover both densely occupied restrooms; credit cannot be earned.
C. Four – Adds monitors to lobby and corridor, which are not densely occupied; not required.
D. Five – Same over-coverage as (C) plus one extra; exceeds credit requirements without added benefit.

References

1. USGBC. LEED v4 for Interior Design and Construction Reference Guide, EQ Credit “Enhanced IAQ Strategies,” Option 2, Part C Carbon Dioxide Monitoring, p. 538-539.

2. ASHRAE Standard 62.1-2010, Table 6-1 “Minimum Ventilation Rates in Breathing Zone,” Occupant Density column: Toilet/Restroom 0.50 pers/m²; Lobby & Corridor 0.05 pers/m²; Front-desk/Service Counter ≤0.25 pers/m².

3. USGBC LEED v4 Definition of “Densely Occupied Space,” Glossary, p. 931.